4/9/2012 9:03 AM | |
Joined: 7/18/2011 Last visit: 10/9/2023 Posts: 521 Rating: (91) |
Hi KaRthickatr, Take a look here for GSD files. Kind regards, BV |
4/9/2012 12:58 PM | |
Joined: 10/7/2005 Last visit: 9/25/2024 Posts: 3022 Rating: (1054)
|
Hello KaRthickatr here's my take on things: 1.) Profibus GSD file for the Profibus DP Master module of the IM151-8 PN/DP CPU: Not available (and not needed, only Profibus DP Slaves have GSD files) 2.) ProfiNet GSD(ML) file for theIM151-8 PN/DP CPUitself: Not available "off the shelf", you create this one yourself from Step 7's HWconfig after you configured the IM151-8 PN/DP CPU as a so called "I-Slave". Have a look at chapter 4.8 of the SIMATIC PROFINET System Description manual which has all the details on how to do so. I hope this helps |
Cheers |
|