Hi Borrowitch, A IM 308C and also the cards of SIMATIC TI can't use DPV1. [:o] Also I/O-cards that uses DPV1 to parametrize won't work, they are not in the GSD-files that works in a IM 308C or DP-Card for SIMATIC TI. You have to use the older GSD-files that are starting with SIEM8xxx.GSE, all other ones won't work!! All the GSD starting with SI018.. and SI028.. are not working on a IM 308C or SIMATIC TI DP-Card. [:(] This is for ET200S/M/L So you need the newest file SIEM806Afrom the file IM151-1AA0x_Std-CU.zip, please be careful with cards that are not in these GSD-file, they won't work. Under http://support.automation.siemens.com/WW/view/en/652154you may find the mentioned file. Best regards, Late |
Last edited by: Late at: 3/18/2006 11:38 PMFile and place to find added Last edited by: Late at: 3/18/2006 11:17 PMI hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|