4/4/2019 11:31 AM | |
Joined: 3/6/2012 Last visit: 11/12/2024 Posts: 155 Rating: (18)
|
Hi N. Vijay Is your input frequency displaying a negative value? will4 |
www.chbdrives.com |
|
This contribution was helpful to1 thankful Users |
4/9/2019 10:19 AM | |
Joined: 3/17/2013 Last visit: 8/25/2024 Posts: 481 Rating: (43) |
Yes Will4 , it is showing -ve value -59.9 Hz See the attachment Regards, Naga |
4/9/2019 10:31 AM | |
Joined: 3/6/2012 Last visit: 11/12/2024 Posts: 155 Rating: (18)
|
If you swap two of the input phases around on the drive this should fix your problem. Regards, |
www.chbdrives.com |
|
4/9/2019 10:36 AM | |
Joined: 3/17/2013 Last visit: 8/25/2024 Posts: 481 Rating: (43) |
Thanks again , let me further dig when it got reversed, as I had snapshots before 1 year showing correct value of input frequency on the same drive. I will update you soon Regards, N Vijay |
4/9/2019 10:53 AM | |
Joined: 3/17/2013 Last visit: 8/25/2024 Posts: 481 Rating: (43) |
Hi Will4, One more clarification please, If I change the input phase sequence will it have any other affects apart from showing correct efficiency. Regards, Naga |
4/9/2019 11:01 AM | |
Joined: 3/6/2012 Last visit: 11/12/2024 Posts: 155 Rating: (18)
|
There wont be any other issues. Regards, |
www.chbdrives.com |
|
4/9/2019 1:54 PM | |
Joined: 3/17/2013 Last visit: 8/25/2024 Posts: 481 Rating: (43) |
Hi Will4 Further digged the history and I noticed this happened since SIEMENS changed input MV Transformer 2 years back. Power cable size is cut to length and no chance of getting swapped. Can it be INPUT attenuator cables reversal. If yes can I Swap that cables please confirm Regards, N Vijay |
4/10/2019 12:54 AM | |
Joined: 3/6/2012 Last visit: 11/12/2024 Posts: 155 Rating: (18)
|
I would check the wiring from the input attenuation resistors is as per the original drawings considering the input transformer has been changed. Also check the wiring from the input CTs is correct as per the original drawings. Regards, |
www.chbdrives.com |
|