7/18/2023 11:47 AM | |
Joined: 8/31/2013 Last visit: 11/8/2024 Posts: 607 Rating: (41) |
Hello, Yes you can communicate via Modbus TCPIP see the attached manual Attachment109779762_LOGO_ModbusTCP_DOC_en.pdf (476 Downloads) |
Warm Regards |
|
7/18/2023 4:42 PM | |
Joined: 12/18/2014 Last visit: 11/9/2024 Posts: 34177 Rating: (4256)
|
Did you have a manual of the detector in PDF or a link to this? |
7/19/2023 7:54 AM | |
Joined: 2/17/2022 Last visit: 5/13/2024 Posts: 14 Rating: (1) |
Hi iox65, I have the manual for the control unit of the detectors (2 in total). M07211-Vortex-Manual-Iss-8-Jan-15.pdf (crowcon.com) Can't upload because it's too big, even zipped I can't connect them straight to the LOGO or I will run out of Analog inputs, which I need for pressure transmitters. I also included the modbus register overview. For me the main problem will be how to use the input for range to something I can use. I think I need the range input (say modbus register nr 123 - value 14, so range 0-20) to determine the maximum of the detector (in this case 20) and use that in combination with the detector level (say modbus register 3000 - value 500) The actual detector readout in this case will be 20*(500/1000) = 10, which has to be lower than my threshold or the alarm will be triggered But I don't know how to program the first bit. Thanks for the help. Regards, Quibusari AttachmentVortex-Modbus-Map.pdf (475 Downloads) |
7/19/2023 11:26 AM | |
Joined: 12/18/2014 Last visit: 11/9/2024 Posts: 34177 Rating: (4256)
|
Maybe the attached diagram helps you.
AttachmentDetecor_0BA8.Standard.zip (537 Downloads) |
This contribution was helpful to1 thankful Users |