4/11/2008 4:01 PM | |
Posts: 5822 Rating: (412)
|
Hello, did you maybe use a CP that does not support ISO Transport Protocol? There are some, especially in the S7-300. Best regards J_Bell |
4/12/2008 6:18 PM | |
Posts: 68 Rating: (0) |
I'm using CP343-1 Lean on the PLC. |
4/12/2008 7:00 PM | |
Posts: 5822 Rating: (412)
|
Hello, I am sorry but the CP 343-1 Lean you use does NOT support the ISO Transport Protocol. Best regards J_Bell |