7/8/2013 8:08 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
Support Request Eventually share the result with us later on. |
7/8/2013 8:43 AM | |
Posts: 153 Rating: (2) |
really we can use 61 1SI cards with IM 151 8 PN/DP???? |
7/8/2013 9:46 AM | |
Joined: 5/28/2008 Last visit: 5/11/2024 Posts: 4506 Rating: (836) |
HelloRaghav, Max. No. of moduels per rack for For HF-IM6ES7151-1BA02-0AB0is 63 module including power modules. But without exceeding 244 Byte Input & 244 Byte Output in addressing area of this IM. and also should not exceed 700mA (backplane current). So, Actual No. of allawable modules depends on:
If you exceed one of the above limits, you should go for another new rack. For Module "6ES7138-4DF01-0AA0", I/O data transmismission setting for each module can beprogrammed 4, 8 or 32 bytes.
Hope this helps. |
Ayman Elotaify |
|
This contribution was helpful to3 thankful Users |
7/9/2013 4:29 PM | |
Joined: 8/30/2007 Last visit: 2/29/2024 Posts: 16 Rating: (0) |
I got it - as far as IM151-1 HF is concerned. However, I could not find any technical specification forIM151-8 CPU ! |
Follow us on