Joined: 8/2/2010 Last visit: 4/1/2024 Posts: 45 Rating: (1) |
Dear All, I am using S7-300 315-2DP & TIM 3V BN (6NH7808-3AA00) V4.1. We eastablished the communication with protocol tester. We are able to send & receive all values. We configured measured values at address 2000 We are receiving all the corresponding values in DB143. If I forced 100 in DB143 I am receiving 100 on tester at addres 2000. If I force 65 in DB143 I am receiving 65 on tester at addres 2000. If I force 64 in DB143 I am receiving 0 on tester at addres 2000. If I force any value more than 64 I am receiving it as it is at address 2000. But If I force any value less than 64 I am receiving 0 at address 2000. I want any value which is forced to be at address 2000. Please tell where I have to set any thing to get this in ParaM file. Find attached my ParaM file for reference. Thanks & Regards AttachmentTIM_2303203.zip (25 Downloads) |
4/13/2011 12:17 PM | |
Joined: 8/2/2010 Last visit: 4/1/2024 Posts: 45 Rating: (1) |
Please guide me in resolving my problem My original problem of Measured Values not receiving less than 65 on IEC 101 is resolved. [schnippschnapp] new question is splitted to How to check communication fail signal of TIM 3V BN (6NH7800-3AA0) with scada or protocol tester. Thanks & Regards |