8/8/2019 12:35 PM | |
Joined: 9/27/2006 Last visit: 9/24/2023 Posts: 12153 Rating:
|
Hello Raj; You are working with a CPU that was taken out of production in 2004, I am glad to see that it seems to be working correctly 15 years later. You should take a few seconds to look at this description of the way the S7-300 memory concept has evolved over the years; in the document attached, your CPU would be covered by Case 3. It has an integrated RAM of 96 kB as Load Memory (see the image below), so you do not need a memory card to download your program to the CPU; however, you need battery support to maintain that memory area when you power off the unit. Using a memiry card as Load memory will simply give you mainteenance of the program memory without a battery. How can you obtain an overview of the memory concept of SIMATIC S7-300 CPUs and C7 devices? https://support.industry.siemens.com/cs/us/en/view/7302326 As per the description of the CPU in the attachment below, it can act as a Profibus-DP master (or slave) through its integrated Profibus port, so you should be able to connect to your Profibus slaves if the integrated port, the network cabling and the Profibus configuration are working. I suggest you take and attach a screenshot of the Hardware Configuration showing us the Profibus slaves and the input/output addresses used for Profibus exchanges; also give us some idea of how you are addressing these slaves in your program. Hope this helps, Daniel Chartier |
8/9/2019 7:48 AM | |
Joined: 5/7/2015 Last visit: 9/20/2023 Posts: 56 Rating:
|
Screenshot of the settings after problem was solved |
Follow us on