Hello all im have big project in Simatic manager - s7 v5.6 sp 2 and wincc flexible 2008 sp5. All programs runnign without problems. In same CP have tiaportal v16 profesional profesional (step7 + wincc ) My project have : 4x cpu 313C -all same. 2x Hmi OP 170B - in wincc change to model 177B (in guide its ok for replace) 2x hmi OP 177B If try migration in in tia V16 after 10% have error. When I check log file, its very dificould for me and can not ,,translate,, where is mistakes and why not completed. Its better try it on tiaportal v11 ? or whre is problem? Thanks all for support. AttachmentLog error.txt (60 Downloads) |
2/28/2022 1:42 PM | |
Joined: 7/9/2015 Last visit: 10/18/2024 Posts: 3987 Rating: (595)
|
Hi, OP177B will not be supported anymore with TIA V15 or newer. So try to migrate with an older TIA Version. In example you can download V14 SP1 trial. Please check this: When upgrading your TIA Portal project to V15 or higher, why do you get this error message: "The device [XY] is not supported in this version."?Regards, Towome |
|
|