3/13/2022 2:26 PM | |
Joined: 9/27/2006 Last visit: 5/3/2024 Posts: 12257 Rating: (2666)
|
Hello gaju; A DP master from any manufacturer does not need to be updated from the slave's perspective. You must provide the Profibus configuration software of the DP master with the gsd file of the slave so it can integrate it in its configuration files. Most slaves have "standard" gsd files, for Siemens you can search for them here on the forum. or example, this list contains the gsd files for a large number of S7 CPUs, IMs and Profibus CPs: https://support.industry.siemens.com/cs/ww/en/view/113652 Other slaves, more complex, will require that you generate them on demand. This for example happens with some drives, when the telegrams have to be adapted for use in your project. In that case you will find the instructions through the forum search box. Hope this helps, Daniel Chartier |
3/14/2022 6:17 AM | |
Joined: 4/4/2008 Last visit: 9/30/2023 Posts: 35 Rating: (0) |
Thanks ChristophD Very Much Please see attachment and please let me know , configuration is correct or not. Regards GAJANAN AttachmentNetwork View.zip (349 Downloads) |
3/14/2022 6:26 AM | |
Joined: 5/12/2006 Last visit: 5/2/2024 Posts: 22243 Rating: (2981)
|
is correct |
3/14/2022 9:42 AM | |
Joined: 4/4/2008 Last visit: 9/30/2023 Posts: 35 Rating: (0) |
Thank You Very much |