6/30/2013 9:47 PM | |
Posts: 9 Rating: (1) |
Hi
I tried and nothing.......
Thanks anyway.
EER
|
6/30/2013 9:58 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Hello, Why don't you try ask your issue here (Support Request).I am sorry for the problem at my earlier post and it was because of language barrier .All snapshots was in french or other langauge that I could not find the keywords easily.Share the remedy in case of conqure! Best regards Hamid Hosseini |
6/30/2013 10:22 PM | |
Posts: 9 Rating: (1) |
It is a great idea hdhosseini I am following your advice about the support request. The language of the snapshots is Spanish. I changed theTIA PortalUser Interface Language to English when I noticed it. Thank you very much for your nice answers. I will post the solution to the problem when I have one. Thanks again. EER |
This contribution was helpful to1 thankful Users |
7/10/2013 7:17 PM | |
Posts: 9 Rating: (1) |
Hi, Hammid, finally, the solution for the problem was found: I created two new tags and linked them to the animations. The new tags used for the animations are now linked to the Connection_1 that is a direct Connection to the PLC. The error was using tags linked to the HMI_connection_1 The weird thing about all this, is that they were not bad configured, at least in the theory, because those tags were linked to the PLC. Thanks and best regards EER AttachmentScreens.pdf (391 Downloads) |
This contribution was helpful to2 thankful Users |