1/11/2013 9:28 AM | |
Joined: 3/14/2008 Last visit: 8/7/2024 Posts: 2080 Rating: (931) |
You have to check if the parameter has the "S7_m_c" attribute...This means it can be used in WinCC |
If I could help you, you can use the RATE button. Thank you. |
|
1/11/2013 1:09 PM | |
Joined: 3/14/2008 Last visit: 8/7/2024 Posts: 2080 Rating: (931) |
Oh sorry, I misread your first post.. Your problem is that the parameter is not defined as a struct... See your APL Styleguide page 47. Make sure that you also add the attribute: S7_xm_c.. This is needed when you use structs on WinCC |
If I could help you, you can use the RATE button. Thank you. |
|
1/15/2013 2:52 PM | |
Joined: 5/18/2006 Last visit: 10/21/2020 Posts: 170 Rating: (64) |
Similar to the Memo Faceplate view, required Tags (#StatusPermanent & #TextPermanent) only get generated when the block Author field begins with ‘AdvLib’. Note Author Field limited to 8 characters and this requirement requires/defines the first 6 characters. (Reference APL Style Guide (10/2012) section ‘Creating project-specific blocks in conformance with APL, Adapting AS Blocks, Memo View’). cabreytj |
This contribution was helpful to1 thankful Users |
2/16/2013 8:10 PM | |
Joined: 6/4/2007 Last visit: 7/17/2024 Posts: 16 Rating: (0) |
Proble solved with "AdvLib". Thank you very much. |
This contribution was helpful to1 thankful Users |