Hello, if you use FW V4.1 on the PLC then yes is possible. For this go in the options of the PLC and activate the Configuration Control . Now you can configure from the userprogram which slot you use. For more information how to use the Config Control refer the Online Help of tia Portal. or check this FAQ: https://support.industry.siemens.com/cs/ww/en/view/29430270