Hi Kbv, your configuration seems to be taken from PCS 7 minimal configurations manual: https://support.industry.siemens.com/cs/de/en/view/24023824 See Chapter 6 of the document valid for PCS 7 V8.0 SP1. But if you really have this use case of minimal configuration there is the very important sentence in chapter 6.1 at the headline "Particular features for programming" : For this reason, we now configure an OS application, open it on both stations, and configure the mutual redundancy respectively local in WinCC. For downloading to the OS Single Station, the Runtime and the OS on the ES must be closed. Regards |