2/22/2013 11:51 AM | |
Joined: 4/22/2010 Last visit: 2/15/2024 Posts: 5697 Rating: (711) |
Hello, Make sure you have the right addressing, look in your hardware config. Standard i believe the digital I/O start at adress 124. Did you connect the 24 V supply to the I/O cards? For connection details: SIMATIC S7-300 CPU 31xC and CPU 31x: Technical specifications Regards, Marcjan |
Last edited by: Marcjan at: 2/22/2013 12:03 PMProblem solved? |
|
2/22/2013 12:32 PM | |
Joined: 5/28/2008 Last visit: 4/15/2024 Posts: 4505 Rating: (835) |
Hello, Did you connected the power feeding for integrated IOs of this CPU?
|
Ayman Elotaify |
|
2/24/2013 9:15 AM | |
Posts: 36 Rating: (0) |
Dear Marcjan Thankyou for your help but I am having no problem in the simatic manager. I have done all the hardware configuration in the Simatic manager. Address for input realy starts from 124 to 126, but problem is with the card somehow i cannot figure out what. Regards Freeze
|
Last edited by: freeze12 at: 2/24/2013 9:23 AM |
|
2/24/2013 9:27 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
Hello, For sure you need power supply for inbuilt I/O. Basically TonVeera suggestion is correct. Wiring of DI/DO - Wire the CPU Wiring of AI/AO - Wire the CPU Wiring of Counters - Wire the CPU Best regards, Hristo Mihalev |
Last edited by: UMENCHO at: 2/24/2013 9:32 AM |
|
2/24/2013 3:01 PM | |
Posts: 621 Rating: (10) |
check backplne connection. |
2/25/2013 8:02 PM | |
Joined: 4/20/2007 Last visit: 2/6/2024 Posts: 724 Rating: (41) |
There is no back plane connection for integrated I/O modules.
|