12/16/2020 6:20 AM | |
Joined: 10/11/2006 Last visit: 8/7/2024 Posts: 5887 Rating:
|
Hello, p1300=15 means the motor module is used as braking module, see chapter 8.14 of the function manual. So this mode must not be used for a motor module a motor is connected to. For using a braking chopper and resistor, you need no special control mode at the motor module. You should only check the settings for the Vdc max controller. |
With best regards, |
|