Joined: 7/7/2010 Last visit: 10/4/2024 Posts: 15264 Rating: (2422) |
I assume you were referring to the information from this Siemens web page: https://support.industry.siemens.com/cs/ww/en/view/101509838/13795110667 It mentions whether or not user interaction is required once the fault problem is corrected (loss of power). If your user already issued a startup command via some button, is it acceptable to keep track of that user button until the power on situation causes the F-DO modules to clear the power fault, and then issue a reintegration request to all the modules. At that point, it forgets (resets) the saved state of the user request. This way, the system gracefully starts up and it completely under control of the user the entire time.
|