Industry Online Support
Technical Forum
11/11/2013 8:50 AM | |
Joined: 2/13/2013 Last visit: 4/23/2024 Posts: 6 Rating: (0) |
Thank you Patrick, but I don't think that it's is the right solution because SFC in not "safe". Thank you Giorgio Facco |
11/11/2013 2:05 PM | |
Joined: 5/18/2006 Last visit: 10/21/2020 Posts: 170 Rating: (63) |
You can use the Safety Matrix optional package.The Safety Matrix is normally configured for Emergency Shutdown (ESD) or Master Fuel Trip (MFT). However, the Safety Matrix can be configured to act as a sequencer. Safety Matrix is used with F-System and is TUV certified to SIL 3. See Application and Tools article: Safety Rated Sequential Start-ups, using SIMATIC Safety Matrix cabreytj |
Last edited by: cabreytj at: 11/11/2013 2:40 PM |
|