5/1/2014 10:31 AM | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Joined: 11/21/2007 Last visit: 6/1/2023 Posts: 2321 Rating:
Hello soussia What are the connection details of the cable between CPU programmer port and MP370 ? Which port are you using for MP370 to PLC communication. ? You should be using IF1A ( TTY ) with following cable :
Cheers Navnag |
There is no such thing as the last bug in a program |
5/8/2014 10:42 AM | |
Posts: 63 Rating:
the connexion and the cable are verified but the problem still. |
5/9/2014 5:36 AM | |
Hello You should check the following : a) Have you selected the correct S5 CPU in Protool Configuration ? b) Have you selected the correct port in Protool Configuration ? ( Pl See Attachment ) c)Is the MP370 Comm port OK ( Is it communicating with another CPU for example ) ? d) Is the CPU Port OK ( Is it communicating with PG or another HMI ) ? Hope this helps Cheers Navnag AttachmentSIMATIC_S5_AS511_Connection.pdf (58 Downloads) |
Last edited by: Navnag at: 5/9/2014 5:48 AMAttachment added There is no such thing as the last bug in a program |
5/9/2014 11:27 AM | |
Thanks BeVee Hello soussia Yes if this is a new setup then you do need to load the Std Function Blocks relevent to your CPU and call them according to the attached, Manual Extract. Order no. 6AV3980-1AA21-0AX0 Hope this helps Cheers Navnag AttachmentS5_Std_Blocks_for_TDOP.pdf (50 Downloads) |