First of all, nice setup. The link below describes the difference between PM and PS and what the configuration options are. https://support.industry.siemens.com/cs/ww/en/view/73191930 You should choose option number 3, which will leave you with max 60 watts for the communication moduls. i'm not 100% sure of the power requirements of those communication moduls but i think 60W is sufficient for this configuration. So put a PS on slot 0, for the backbus power and add a PM or any 24V source to power the CPU, set the CPU to "Connection to supply voltage L+". please be aware that a PM has no connection to the backplane bus. I've added a picture which shows you a setup which gets you the most power to the backplane bus. Hope this answered you question? |
Last edited by: Jen_Moderator at: 08/24/2020 07:24:46Optimized link. //Jens |
|
8/24/2020 1:07 AM | |
Joined: 7/12/2019 Last visit: 12/7/2022 Posts: 27 Rating: (0) |
Thanks for the answer. Can I know the original document of the attached photo?
|
8/24/2020 2:30 AM | |
Joined: 9/27/2006 Last visit: 9/16/2024 Posts: 12282 Rating: (2684) |
Hello jjjinl; The link proposed earlier by Veuleman.Jens contains this line: Further Information Open this manual, it has a section named System Overview (of the S7-1500, ET 200MP systems) where you can find this information: https://support.industry.siemens.com/cs/ww/en/view/59191792/125951469579 The chapter named Application Planning has also a few interesting pages discussing PM and PS usage. Hope this helps, |