5/30/2012 1:10 PM | |
Posts: 1 Rating: (0) |
I Have a Pressureswitch from SMC ISE30-A-01-F and also a ISE30-A-01-G. I have a 24VDC 0VDC and 1 analog messure wire. I using the analog card 6ES7134-4JB51-0AB0 for the ET200S. But I don't know how i must connect that. Who can help me?AttachmentZSE30A-ISE30A_EU.pdf (27 Downloads) |
5/31/2012 8:25 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (306) |
Hello, The Analog input module you are mentionning is a 2 inputs (3- and 4-cable connection) / 4 inputs (2-cable connection) for resistance thermometers or resistance measurement. Used typically to measure temperatures. see: http://support.automation.siemens.com/WW/view/en/25546012 The pressure switches you show us deliver a voltage or a current. Seems me that you have got a wrong combination. |
Last edited by: jklm at: 5/31/2012 8:27 PMBest regards |
|