Joined: 3/4/2014 Last visit: 4/13/2023 Posts: 13 Rating: (0) |
Dear Sir, I have the same problem today during motor ID stationary measurement, F30021 comes up, after motor and MoMo output cable to motor isolation check, both are ok, the resistance of inverter phase to ground is about 10 Mohms for all three phase using multimeter, with p1272=on and 1300=0 speed setponit=50rpm without motor cable connected there is no fault message, each phase to ground voltage is 37V AC, so can this prove that all the IGBTs are ok, and which can lead to fault F30021? than you for your help! ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 8/13/2015 11:20:10 AMNew subject after splitting |
|
8/17/2015 5:53 AM | |
Posts: 1529 Rating: (203) |
Does it make a loud banging noise when you try the measurement? Make sure your motor cable phases are not reversed (U-U, V-V, W-W) and that the encoder is not reversed. |