5/29/2012 7:25 AM | |
Joined: 3/24/2009 Last visit: 7/9/2024 Posts: 535 Rating: (112) |
Dear skwr, the VALUE-input of the F_CH_AI must be connected to a tag (eg. IW256). When you compile the program with the option 'generate module drivers', the F_CH_AI will be connected to the module-driver F_PS_12. Afterwards you will be able to modify the input in PLCSIM. For more details have a look at the manual, chapter 'F-I/O access'.
Best regards, yy1 |
5/30/2012 8:52 AM | |
Joined: 3/24/2009 Last visit: 7/9/2024 Posts: 535 Rating: (112) |
Dear skwr, there seems to be an F-STOP on your PLCSIM (quality-code = 16#00) Please have a look at your diagnostic buffer. Maybe your cycle-time is too long?? Best regards, yy1 |
6/1/2012 6:10 PM | |
Posts: 8 Rating: (0) |
Maybe they should be in other OB's? Not default OB35?? |
6/5/2012 6:36 PM | |
Posts: 8 Rating: (0) |
Next question - is it SFC scheme obligatory when using CFC? Or it is possible to simulate program in CFC without SFC? |