Hi! I have a Problem with RF310R and Transponder R320T. All look fine untill I try to read or Write to Transponder. I get the errorcode E1FE03 and Get red flashing light. Im new with this so I dont know what to do Ive tryed a lot. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 6/30/2017 1:19:31 PMNew subject after splitting |
|
6/30/2017 4:21 PM | |
Joined: 10/1/2013 Last visit: 5/8/2024 Posts: 605 Rating: (71)
|
Hi Thimberg, try reading/writing from addrTag (start address) "FF00". The maximum reading/writing length (lenData) for RF320T = 20 byte. This is related to the tag type you use. To understand why just check for the system manual RF300 chapter "7.1 Memory configuration of the RF300 transponders": Hope this helps. |