Posts: 3 Rating: (0) |
Hi Guys, I have the following question . I am have trouble with Siemens voltage monitoring relay 3UG4616-1CR20, i am getting the below defects and also i am attaching the test report so you guys can understand the problem. Attachment-1 => Relay Test report Attachment-2 => Manual – Graph Defect details => OV contact is getting operated during UV conditions which is not in line with the graph clouded in Manual Graph. AttachmentRelay Test report.pdf (215 Downloads) |
9/28/2015 1:24 PM | |
Posts: 467 Rating: (59)
|
Hello Ayekami,
The OV and the UV contact can be operated together if you have a phase failure. See attachment regards LesPaul Attachment3UG4.pdf (222 Downloads) |
9/29/2015 11:44 AM | |
Posts: 3 Rating: (0) |
Hi Paul, Thanks for your reply,you have responded against phase failure not for under voltage condition, your response against phase failure is noted and relay is working fine against phase failure as per the graph.Whereas our problem is relay is not working during UV condition as per the graph you sent . (OV contacts should not make). In addition, we have once again attached our test report for your review and during UV condition phase were not failure but only voltage level of the phase was below the setting voltage as mentioned in the test report and the test was carried out which phase voltage separately.
Waiting for your reply. AttachmentRelay Test report.pdf (225 Downloads) |