2/14/2017 2:41 PM | |
Joined: 1/4/2007 Last visit: 10/11/2024 Posts: 1146 Rating: (175)
|
Hello electro Hamad, Is the red LED “SF” on or off at your Siwarex U module? Best regards Siwarexi |
2/15/2017 6:17 AM | |||
Joined: 5/8/2016 Last visit: 2/15/2024 Posts: 167 Rating: (13) |
the SF LED is off and my fb 45 execute all commands except the command input code :
when i try to execute this command the problem happened and the error shown with error code 1 |
||
A lot of potential remains |
|||
2/16/2017 9:52 AM | |
Joined: 1/4/2007 Last visit: 10/11/2024 Posts: 1146 Rating: (175)
|
Hello elctro hamad, Command “1” is not! the “zeroing”-command. Command “1” is a command for the calibration of the scale (=zero-point of the scale). Command “3” is the “zeroing”-command. I have one question: Do you want to do a new calibration OR do you want to do a zeroing? Best regards Siwarexi |
2/16/2017 11:23 AM | |
Joined: 5/8/2016 Last visit: 2/15/2024 Posts: 167 Rating: (13) |
hello siwarexi i need to re calibrate by using input command "1" but error happened as i told you before with error code 1 |
A lot of potential remains |
|
2/16/2017 4:55 PM | |
Joined: 1/4/2007 Last visit: 10/11/2024 Posts: 1146 Rating: (175)
|
Hello elctro hamad, The error means that there is something wrong with your current calibration digits. I recommend you to reset at first the “adjustment digits 0” and “adjustment digits 1” to “0”. You can find these two parameters into the DR3. The value “0” is the factory setting of these two parameters. Afterwards you can execute the command “1”. After that, put the calibration weight on the scale and execute the command “2”. the calibration is finished now. Best regards Siwarexi |
2/18/2017 6:53 AM | ||||||||||||||||||||||||||||||
Joined: 5/8/2016 Last visit: 2/15/2024 Posts: 167 Rating: (13) |
Dear siwarexi but how can i reset the adjustment "0" and adjustment "1" to zero and these registers of ADC with theoretical maximum terminal value for adjustment digits is 60074 and
and if that possible to set the zero and span of AD0 and AD1 to zero that means , i need to set the adjustment 0 again to certain digital value and adjustment 1 to certain digital max value again !! check the below sentences: ...After the analog-digital conversion of the measured voltage, the zero point is assigned to the digital value (adjustment digits for the adjustment zero) with the command "Adjustment zero valid (1)". what do you think ?? best regards Hamad
|
|||||||||||||||||||||||||||||
A lot of potential remains |
||||||||||||||||||||||||||||||
2/20/2017 6:44 PM | |
Joined: 1/4/2007 Last visit: 10/11/2024 Posts: 1146 Rating: (175)
|
Hello elctro Hamad, “but how can i reset the adjustment "0" and adjustment "1" to zero” Well, you use the FB45 in your S7-program. Do the following steps: 1. Execute command code “203”. Command code “203” means: “Read the DR3 from the Siwarex U to the DB_Scale”. 2. Change into the DB_Scale the “Adjustment digit 0” and “Adjustment digit 1” at the addresses DBW54 and DBW56 (both to “0”). 3. Execute command code “403”. Command code “403” means: “Write the DR3 from the DB_Scale to the Siwarex U module”. Afterwards you can do the calibration with the command codes “1” and “2”. After that you can read once again the DR3 with the command code “203”. Now you will see that the current digit values will be in the range of 5461 … 60074 digits . Best regards Siwarexi |
2/21/2017 6:32 AM | |
Joined: 5/8/2016 Last visit: 2/15/2024 Posts: 167 Rating: (13) |
hello Siwarexi i will try to this and i will give you feedback best regards |
A lot of potential remains |
|