10/22/2015 7:15 PM | |
Posts: 10 Rating: (0) |
Hello, I have an other question, can I use one or two pulse relays to adjust the valve motor on my heating system? I have tried to describe it in the attached pdf, I am using a LOGO! 24CEo,OBA8 with AM2 RTD, AM2AQ and DM8 12/24R Kind regards Stefan AttachmentNext attempt.pdf (333 Downloads) |
10/23/2015 8:47 AM | |
Posts: 2930 Rating: (432)
|
Hi, it looks like you are a beginner in LOGO! Right? To your question: Basically at least with the Relay outputs you should be aqble to control your Belimo. But you may need a protection for the Relay outputs because of inductive load. Hope this helps |
10/24/2015 2:32 PM | |
Joined: 12/18/2014 Last visit: 10/10/2024 Posts: 33927 Rating: (4217) |
I once created you a program for controlling a mixing valve. With the attached Excel spreadsheet, you can determine the necessary parameters for your individual heating curve and then change in the logo program. AttachmentMixing valve.zip (394 Downloads) |
10/25/2015 10:04 AM | |
Posts: 10 Rating: (0) |
1) If I understand you correctly, you need a program that controls the mixing valve for your heating system. The mixer valve does not operate analog but digital. Correctly? Partly correct, the valve actuator operates on 24V AC, and runs on pules from two relays todady, one relay for more heating and the other for less heating, see attached pdf. 2.) You want to pretend about the TDE a target value for the mixing valve, but which is dependent on the outside temperature and the desired room temperature. This is to be automatically calculated. Correctly? That's correct, but I also have a second actuator that regulates the amount of incoming air, that is to be heated with the water from the 1. above, there is also another actuator that regulates the amount of air that should go out of the house, this last regulator is regulated with 0-10 Volt, and that is working thanks to your program from earlier questions. 3.) What are the parameters you want to pretend? I want to be able to manually regulate the inner temperature, and also the amount of in and outcoming air. This of course only if the system is not compensating fast enough( due to fast falling outer temperature) AttachmentM24-5_M22-53.pdf (378 Downloads) |
Last edited by: Stefansvets at: 10/25/2015 10:50:26 AMForgot attachment |
|
This contribution was helpful to1 thankful Users |
11/8/2015 8:16 PM | |
Posts: 10 Rating: (0) |
Helllo again, I now have tried to make this work as i want, and some things work ok, but i have a small issue, I can't get the temperature values to behave! I have tried to change values but I always get strange read values. Any good Ideas to solve this? there seems to be a lot of good ideas in this forum.... Kind regards Stefan AttachmentMixing valve adjusted.zip (346 Downloads) |
11/9/2015 6:08 AM | |
Joined: 12/18/2014 Last visit: 10/10/2024 Posts: 33927 Rating: (4217) |
I do not know why you changed the set of my parameter values for the analog amplifiers. I have corrected again and the new analog input to the PI controller also adjusted. AttachmentMixing_valve_V2.zip (368 Downloads) |
Last edited by: ixo65 at: 11/9/2015 6:20:20 AM |
|