5/3/2012 4:00 PM | |
Joined: 8/31/2010 Last visit: 4/14/2024 Posts: 1509 Rating: (222) |
Hello Sardar99, Check these for your requirement Communicating with PLC - Modicon Modbus TCP |
Like it? Rate it! |
|
5/9/2012 7:20 AM | |
Joined: 10/3/2010 Last visit: 4/25/2024 Posts: 1552 Rating: (188) |
If the third party device doesn't work, it might mean that they've change the free and open source protocol, so in fact, they claim to communicate via Modbus but the standard Modbus protocol has been changed. Anyway, I would always try it for all possible CPU types. Heplfull programs (when you understand the Modbus telegrams) to test/check communications are ModScan32 and Wireshark. |
B r g d s , |
|
5/9/2012 3:25 PM | |
Joined: 10/3/2010 Last visit: 4/25/2024 Posts: 1552 Rating: (188) |
About filtering Modbus in Wireshark: link Brgds. |
B r g d s , |
|
This contribution was helpful to1 thankful Users |
5/10/2012 7:11 AM | |
Joined: 10/3/2010 Last visit: 4/25/2024 Posts: 1552 Rating: (188) |
In an older thread, someone managed to communicate with a non-Schneider device too HERE Brgds. |
B r g d s , |
|
10/9/2018 5:09 PM | |
Posts: 25 Rating: (0) |
This link doesnt work. Could you please update it? |