10/5/2015 12:29 PM | |
Posts: 25 Rating: (0) |
Hello hdhosseini, Thanks for your help! i was able to read and write values to MVI56 Master module using the I and Q registers. Just wanted to know, do we use any SFC14 & SFC15 to read write values in this case. as we do not have any master configuration in the Siemens Hardware, its just treated as DP salve the CPU315? Thanks, VJ ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 10/7/2015 3:16:27 PMNew subject after splitting |
|
10/6/2015 5:18 PM | |
Joined: 1/28/2009 Last visit: 4/26/2024 Posts: 6838 Rating: (1359) |
Hello again, It doesn't matter that master is configured in your current project.PROFIBUS-DP is a open and deterministic.It means when master and slave are configured accordingly , all request by master will be answered properly by slave via PROFIBUS telegrams. To use SFC14/15 you need consistent data , the volume should be greater than 4 bytes( or 3 byte) and it is considered as a whole.See the attached file.When you configure slave like that,Same setting should be selected in master. I hope this helps, hdhosseini Attachment4.rar (110 Downloads) |
Follow us on