12/7/2022 12:34 PM | |
Joined: 9/23/2005 Last visit: 9/18/2024 Posts: 4704 Rating: (721)
|
The manual says: The CTRL_HSC_EXT instruction measures the Frequency using the same measurement technique as Period mode to find the ElapsedTime and EdgeCount. The instruction calculates the frequency as a signed integer value in Hz using the formula: Frequency = EdgeCount/ ElapsedTime
If you require a floating-point value for frequency, you can use the above formula for frequency
when the HSC is in Period mode. Note that in Period mode, ElapsedTime is returned in
nanoseconds and can require scaling of the value. |
Regards, |
|
12/8/2022 7:30 AM | |
Joined: 1/13/2022 Last visit: 7/5/2023 Posts: 2 Rating: (0) |
Hello, I Tried HSC in Period, and it works ! Thank you ! |
Last edited by: SALMA DHF at: 12/08/2022 07:31:22 |
|
Follow us on