4/20/2014 11:24 AM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (308) |
HelloEgbert Jan, You have ET200S connected to the H station through aY-Link. So, both CPUs can access the IO modules in the ET200S. This is not the same with central IOs (e.g. the DO module in Rack 0). If CPU in Rack 0 fails, CPU in Rack 1 won't be able to write the outputs in this module. To come over this problem, 1- You can move these outputs to one of your ET200S stations. OR 2- Add another central digital output module in Rack 1. In this case you will have to connect your outputs through diodes (Check Pages 156 & 432 inS7-400H manual).
Yes, this is right, 422-1BL00 is not listed in the module list supporting IO redundancy. However, you can still use it. At the end of your program just move the output words of the 1st module to the output words of the redundant module. Best regards, H-H |
Follow us on