6/28/2013 6:32 AM | |
Posts: 81 Rating:
|
Hello Mr. kumar You are correct, we have to downlad in master CPU & slave CPU gets cordinated with sync cable & gets started automatically. regards, Manoj
|
6/28/2013 6:35 AM | |
Posts: 81 Rating:
|
hello amit, I think you didnt find attachment in my last post. I have mentioned in that all this info Please find attchment regards, manoj
AttachmentWARM_RESTART.pdf (366 Downloads) |
6/28/2013 7:07 AM | |
Joined: 9/16/2011 Last visit: 6/20/2024 Posts: 291 Rating:
|
Dear, DS SURESH KUMARis absolutely right, we need not to download the program in both PLC, it should be downloaded in rack-0 PLC ONLY. And on connecting the FO patch cord between the plc, the rack-1 PLC will sync with the rack-0 PLC automatically. But one more thing to be noted here is that it may few minutes (i.e 5-10 min) to sync depending on the program size. so my advise tohexeis, First download the program only in rack-0 PLC, while turning off the rack-1 PLC or by disconnecting the FO patch cord. After downloading, kindly turn on the rack-1 plc or connect the patch cord. Wait of sometime to synchronize. Reg, Ashish
|
Reg, |
|
6/28/2013 8:21 AM | |
Joined: 11/18/2010 Last visit: 8/5/2022 Posts: 523 Rating:
|
hi suresh, we have to download HW configuration to both PLC not software? regards, viral |