9/12/2008 3:14 PM | |
Posts: 487 Rating: (45) |
Did you try putting PLC to run from the mode switch on CPU? If yes, can you post info from Diagnostic buffer? |
Last edited by: JMJ at: 9/12/2008 5:28 PM |
|
9/12/2008 5:23 PM | |
Joined: 10/31/2005 Last visit: 9/4/2024 Posts: 366 Rating: (31) |
You'll have to put PLCs in RUN-P mode via STEP 7 (PCS7) since newer CPUs doesn't have hardware switch position Run-P. |
6/27/2013 6:11 PM | |
Posts: 81 Rating: (2) |
Dear experts, I have S7 H station 414H CPU. In those CPUs, rack 0 CPU is working perfectly but rack 1 CPU is not going to RUN mode. 1. I reseted memory through hardware as well as through software. 2. Download individually as well as at both time in both CPUs. 3.When i went to start through warm/cold restart, it shows THIS ACTION IS NOT PERMITTED even my switch is in RUN position only. Please find attchment WARM RESTART PAGE NO 2 When i clicked on HELP this page got open. Please find attchment WARM RESTART WARM RESTART PAGE NO 1. It is not going to RUN even after memory reset. what will be problem?? regards, manoj
AttachmentWARM_RESTART.pdf (874 Downloads) |
6/27/2013 7:37 PM | |
Posts: 81 Rating: (2) |
Hello, I have done downloading in both PLCs. But it is not going into start mode. Please find attachment, it shows diagonstics & help of the same. It is showing I/O error but same programe is getting downloaded in rack 0 CPU. There is no problem in programe as well as in hardware configuration. It is perfectly running in rack 0 CPU. regards, manoj
AttachmentDiag.pdf (903 Downloads) |
Follow us on