Hello Stefano, In brief YES you can. WinCC RT advanced! You mean WinCC TIA?! If this is the case then you can have a look on Connecting SIMATIC HMI Panels with SIMATIC S7-400H (WinCC V13 and STEP 7 V5.5)If you have just WinCC loaded to your IPC then you can, 1- Manage connection switching by some scripts (I remember there was a ready made wizard in WinCC but I can't remember the name). You will have a switching time over 5 seconds. 2- Create a fault-tolerant connection between WinCC(PC) and the H-station. You can follow the same procedures as per this link. You will just replace the user application with WinCC application. You will also need a SOFTNET REDCONNECT license. In this case switching over will be bumpless. Best regards, H-H |
This contribution was helpful to1 thankful Users |
4/13/2016 11:49 PM | |
Joined: 5/28/2008 Last visit: 10/29/2024 Posts: 4516 Rating: (839) |
Hello, I think this link may be helpful: |