2/25/2014 11:42 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
|
Hello, Hello, It's allowed to wire 2 1BL00 modules in paralel for redundant load connections, this module has no diagnostics. See SIMATIC S7-400 S7-400 Automation System Module Data for more details of both cards. Regards, Marcjan |
Problem solved? |
|
This contribution was helpful to
1 thankful Users |
2/25/2014 5:13 PM | |
Joined: 1/28/2009 Last visit: 7/15/2024 Posts: 6844 Rating:
|
Hello, In the following FAQ you can find the whole list of modules (central/decentral) that support I/O redundancy for an H configuration: Redundant I/Os with S7-400H systems Best regards, Hamid Hosseini |
Last edited by: hdhosseini at: 2/25/2014 5:19 PM |
|
This contribution was helpful to
1 thankful Users |
2/26/2014 6:39 AM | |
Joined: 8/27/2006 Last visit: 7/21/2024 Posts: 719 Rating:
|
Thank you Hamid. That settled the issue if the entry is still valid (note that it is from 2004) 422-1BL00 does not support redundant DO, only 422-7BL00 does, as the entry stated.
|
The more you know, The more you know that you don't know |
|
This contribution was helpful to
1 thankful Users |
2/26/2014 7:10 AM | |
Joined: 1/28/2009 Last visit: 7/15/2024 Posts: 6844 Rating:
|
You are welcome AMAZINGAHMED , It is not difficult to check if the list is valid now.In section 13.14.1 of the manual for the Fault-tolerant CPUs( V6 -->2013-10-22) ,you can find a similar list.You can check both or even a newer reralease of H CPU manuals.
Best regards, Hamid Hosseini |
Last edited by: hdhosseini at: 2/26/2014 7:12 AM |
|
This contribution was helpful to
2 thankful Users |