6/29/2013 4:38 PM | |
Posts: 559 Rating: (87) |
Dear N.Tufail, Are you using any AI module or you are using the inbuilt input of 224 XP? Just use 0-10V Supply & connect it with two End Terminals of 1 kohm Pot & Variable Terminal of Pot to V of PLC & the Negative Terminal of POT (which is connected to M of 10V supply), connect it to M of AI of PLC. Now if you vary the POT you must get change in counts of AIW 0. If it is OK. Then you can make logic as per your requirement. Attachments7200_224xp_schematic.pdf (428 Downloads) |
This contribution was helpful to1 thankful Users |
7/1/2013 2:20 PM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating: (272) |
Hello, you can use following Scaling block as explained by other friends. Please find attachment. You have to insert this library in your Microwin Software to read the counts from Analog input and to scale in required Range. Hope this helps. Attachmentscale.zip (397 Downloads) |
Last edited by: Amit_86 at: 7/1/2013 2:24 PMLast edited by: Amit_86 at: 7/1/2013 2:22 PMVANDE MATARAM..... |
|
7/1/2013 2:35 PM | |
Joined: 3/18/2008 Last visit: 12/8/2023 Posts: 1750 Rating: (272) |
Hello, You can refer following Block codes to acheive your requirement. PLC will get counts value in AIW0 in this case i.e. 0 to 32767 corrosponds to 0-10 V. Please go throgh it. Hope it helps. Attachmentlogic.zip (365 Downloads) |
VANDE MATARAM..... |
|
Follow us on