11/23/2013 12:12 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, you are looking for a older type TC module, this is the newer one 6ES7231-7PD22-0XA0 The mentioned Phoenix Contact or P&F are signal converters TC in 0-10V or 4-20mA out. Regards, Marcjan |
Problem solved? |
|
11/24/2013 8:49 AM | |
Posts: 44 Rating: (0) |
what stands for P&F and MTL ? which one is easy to implement and which one is less expansive? |
11/24/2013 3:05 PM | |
Joined: 9/27/2006 Last visit: 9/18/2024 Posts: 12282 Rating: (2684) |
Hello N.Tufail; P&F and MTL are companies that produce, amongst other things, signal conditioners. It would have been very easy for you to simply Google the name to find the company. I have located for you the 3 websites of the companies suggested earlier, with links to their TC to 4-20 mA signal conditioners, where available.: P&F: Pepperl + Fuchs MTL: MTL Instruments http://www.mtl-inst.com/product/customised_solutions Phoenix Contacts: https://www.phoenixcontact.com/online/portal/us?uri=pxc-oc-temdetail:pid=2902851&library=usen&pcck=P-13-01-05&tab=2 |
This contribution was helpful to2 thankful Users |
Follow us on