Has anyone had success simply conecting PROFINET to a 4G modem/router and bypass all of the intermediate PC's? |
3/1/2016 10:06 AM | |
Joined: 5/12/2006 Last visit: 11/7/2024 Posts: 22439 Rating: (3029)
|
can you make a short list of the complete IP Settings: 1.) IP Settings from PLC 2.) IP Settings for PC which is connected to the PLC Network 3.) Route command from the PC which should connected to the PLC Have you check the Ports settings in the Firewalls?
Christoph |
Last edited by: ChristophD at: 3/1/2016 10:07:17 AM |
|
3/2/2016 2:16 PM | |
Joined: 3/19/2010 Last visit: 10/26/2024 Posts: 438 Rating: (12) |
Hi, 1) All my PLC's are on dummy 192.168.0.xxx adresses. For example 192.168.0.1 2) PC is 192.168.0.97 on the main network card. PC is connected to Internet over additional USB network card. VPN connection over Teamviewer is properly established, I can ping 192.168.0.97 from my engineering station connected to Internet and VPN of Teamviewr, with the routing PC. But I cannot ping 192.168.0.1 (PLC) 3) route add 192.168.0.1 mask 255.255.255.255 7.157.31.180 metric 1 7.157.31.180 is VPN IP of the PC I am reaching. My firewall is turned off on both PC's, and the routing PC is behind the proxy, but the proxy parameters are set in Teamviewer options. It wouldn't work at all if it was not. Best regards, |
3/3/2016 10:36 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
New question published by Prian is split to a separate thread with the subject Problem to connect to Simotion. Best regards |