Hi, but if I need to rewire merker with DBy.DBx, How can do it??? Thank you in advance for your answer ------------------------------------------------------------------------------------------ |
Last edited by: dstudio at: 07/17/2020 11:45:23Last edited by: dstudio at: 07/17/2020 11:45:38Last edited by: dstudio at: 07/17/2020 11:46:46Last edited by: Jen_Moderator at: 07/17/2020 12:45:39New subject after splitting |
|
7/19/2020 3:09 PM | |
Joined: 4/28/2015 Last visit: 2/7/2024 Posts: 10533 Rating: (821) |
Hello,
it depends on more conditions, optimized or not optimized DB, maybe also used PLC HW. I try give you easy example in case of not optimized DB. You need find offset of your bit, f.ex. it is on 20-th ofset inside DB 100 so you can write DB100.DBX 20.0 In case bit is part of Byte f.ex. and is 3-rd what you need, then DB100.DBX 20.2 Everytime you need count offset position and real bit number. |