12/3/2019 8:26 AM | |
Joined: 2/7/2018 Last visit: 3/14/2023 Posts: 181 Rating: (30)
|
Hi, The SIMOTICS 1FK2 Motors for the SINAMICS S210 are all fitted with absolute encoders Single- or Multiturn. Depending whether you are using a Single- or Multiturn encoder you have to choose the encoder settings in the TO of the S7-1200. Attached you will find which values you have to set. Additional hint: The 14th position of the Article No. of the 1FK2 motor shows the encoder type (S = Singleturn / M = Multiturn). Your motor Article No. is1FK2103-2AG10-1MA0, therefore a Multiturn encoder. Further information about the article No. can also be found in the official catalogue: https://support.industry.siemens.com/cs/ww/en/view/109754381 Best Regards, |
This contribution was helpful to1 thankful Users |
12/4/2019 11:17 AM | |
Joined: 3/8/2017 Last visit: 8/29/2023 Posts: 13 Rating: (0) |
|