Hello Andrrw; If you are confident the software backup you have corresponds to the one on the PLC, then there should be little problem in transfering the program to your MMC. You should never insert or remove the MMC while powered-on so shut down the CPU before inserting it. First does your spare MMC already contain a program for a different PLC ? In that case proceed to a memory reset using the switch on the front of the CPU. This document explains the procedure: https://support.industry.siemens.com/cs/us/en/view/29801950 Also make sure the size of the MMC is able to hold the program tou want to download. How many bytes does it state on the front of hhe MMC? Then simply download the program to the PLC, it will be loaded to the MMC as part of the process. Hope this helps |