1/2/2016 1:33 PM | |
Joined: 3/14/2015 Last visit: 5/6/2022 Posts: 2 Rating: (1) |
Hi I have a s5-945 cpu connected to a PC with ProTool rt, in ProTool I should have a lamp turnt on when E12.5 is on I can not get it to work see enclosed picture does anyone have an idea ON the PLC you see 12.1 and E12.5 is on but looking status E12.0 and E12.7 is on why is that I have make the lamp as showen on youtube.com protool 07 (attributes) AttachmentDownloads.zip (312 Downloads) |
Last edited by: Tidemand at: 1/2/2016 4:12:08 PMLast edited by: Tidemand at: 1/2/2016 10:48:29 PM |
|
1/11/2016 5:41 PM | |
Joined: 3/14/2015 Last visit: 5/6/2022 Posts: 2 Rating: (1) |
I have found a document that tells how to do, there is nothing in the manual ProTool which tells how to do here is an example: Address in S5: MW n = MB n + MBn+1 Address in WinCC Flexible: FW Even bit address in S5: Mx.y Bit address in WinCC Flexible: FWx.y+8 Un-even bit address in S5: Mx.y Bit address in WinCC Flexible: FWx-1.y Examples: Bit address in S5: M4.2 Bit address in WinCC Flexible: FW4.10 Bit address in S5: M5.6 Bit address in WinCC Flexible: FW4.6 Notice in the example how the addresses are within one word in both platforms, but the bit numbering is swapped. I've tried and it works in practice AttachmentHOWTO_setup_and_connect_panel_to_S5 (2).pdf (409 Downloads) |
Last edited by: Tidemand at: 1/11/2016 5:49:59 PM |
|
This contribution was helpful to1 thankful Users |