9/16/2011 9:20 AM | |
Posts: 13 Rating: (0) |
Dear All, How can i check the interrupt time of OB13 in my running S5 PLC 115u ? Can I check it with Step5 software ? Please guide me. Thanks & Regards, |
9/16/2011 9:56 AM | |
Joined: 10/7/2005 Last visit: 10/5/2024 Posts: 3024 Rating: (1054)
|
Hello micron_761 the call intervall for OB13 in a 115U is either declared in DB1 or set by writing to System Data word 97 (if neitheris done, the default call intervall of 100ms applies). Do a search for OB13 in the S5-115U Programmable Controller manualto find the various chapters that have more details on this. If still unsure, you could also simply program an integer addition into OB13 (add 1 to afree Flag or Dataword), monitor the value for a certain time and determine this way the call rate of it. I hope this helps |
Cheers |
|
9/16/2011 10:42 AM | |
Posts: 13 Rating: (0) |
Thanks fritz for your prompt reply, |
Last edited by: micron_761 at: 9/21/2011 6:44 PM |
|
9/16/2011 12:29 PM | |
Posts: 13 Rating: (0) |
Thank you very much BeVee for guiding me. Now I understand the interrupt time. |
This contribution was helpful to1 thankful Users |