Hello, here are the remedy for F7493:
For example I am using 10000LU = 1mm if I reduce it to 1000LU=1mm it can not feed the correct size. (1000 LU = 1mm => 1LU = 0,001mm). Maybe Modulo is a solution. 7.2.1 Setting the mechanical system F7450 standstill monitoring error. standstill window is set to 1000LU(0,1mm) => Trace your positionvalue to evaluate your controller settings and your encoder signal. Use a encoder with a higher resolution and suit your controller settings. P2572 AND 2573 is set to 120000. Unit is 1000 LU/s² !!
Manual: https://support.industry.siemens.com/cs/ww/en/view/109763150 Example: https://support.industry.siemens.com/cs/ww/en/view/109747750 |
|||