roCkber, The distributed controller, is a ET200SP cpu. So you have 2 devices in 1 component (the CPU and IM155-6PN). The et200sp i/o cards can be directly connected to the controller as the et200sp backplane/busbar is onboard the cpu. So you place the distributed controller on the position where you were planning to place the IM155-6PN. The position of the 1217 becomes free. You can also find information about SIMATIC Distributed Controllers here The S7-1217c CPU is actually only for companies that have TIA portal Basic instead of professional and need to programa larger program only once. Else the 1500 series are much more efficient. I assume you have TIA Portal Professional as you mention a Comfort panel and SCADA. Did you already select a SCADA system, or do you just need a remote PC that actually needs to have the same functionality as the comfort panel. When it needs to have the same functionality you have 2 options:
For real SCADA Siemens provides WinCC Professional Runtime for installation on a PC or SCADA server, also in here you can program the SCADA in TIA Portal with a WinCC Professional engineering licence. As WinCC professional is in the TIA Portal it is not the same as any other WinCC you cannot just copy and past your Comfort panel to the SCADA project, you will have a lot of challenges as the setup is different. (exact runtime and engineering licence is depending on the number of powertags you will use) |