2/23/2012 5:03 PM | |
Joined: 8/31/2010 Last visit: 4/14/2024 Posts: 1509 Rating: (222) |
Hello GOG, Yes, S7-1200 supports PROFIBUS DP communication. You can use S7-1200 both as PROFIBUS DP Master (using CP1243-5) and / or PROFIBUS DP Slave (using CP 1242-5). Check here for more details - PROFIBUS in S7-1200
|
Like it? Rate it! |
|
This contribution was helpful to1 thankful Users |
2/25/2012 3:11 PM | |
Joined: 8/31/2010 Last visit: 4/14/2024 Posts: 1509 Rating: (222) |
Hello GOG, You are welcome Ideally the CM1243-5 is going to take care of the PROFIBUS communication without involving more of the CPU. So any CPU can do and i suggest you choose the CPU based on your * Central IO requirement * Work Memory / Load Memory requirement * Type of on-board IO (either DC/DC/DC or AC/DC/Relay or DC/DC/Relay) * requirement on Future expansion of Central IO You can make use of the Online SIMATIC Selection tool to configure your system (shall provide the link in some time as the site is down for maintenance activity) |
Last edited by: Ganes10 at: 2/25/2012 5:44 PMadded the URL for SIMATIC Selection Tool Like it? Rate it! |
|
2/26/2012 12:07 PM | |
Posts: 40 Rating: (0) |
|
Last edited by: Dob at: 2/26/2012 12:08 PM |
|
2/26/2012 2:20 PM | |
Joined: 8/31/2010 Last visit: 4/14/2024 Posts: 1509 Rating: (222) |
Hello Dob, 1. PROFIBUS DP Master is one of the Communication Module not a signal module (I/O module). [every CPU supports max of 3 Communication Modules, which is placed in the Left side of the CPU] 2. In Hardware Confoguration of STEP 7 v11, you have to follow this - Configuring a DP master and slave device Additionally if you are completely new to S7-1200 / it's communication this Easy Book manual should help - SIMATIC S7-1200 Easy Book (dowloadable pdf) / SIMATIC S7-1200 Easy Book (online version) |
Like it? Rate it! |
|