Hi ! I try to do a connection between 2 PLCs S7-1214C with TIA Portal V13. I do the configuration in PLC 1 with a the bloc PUT to send a bool to PLC 2. I use a FB to generate a clock pulse and I permit the access with PUT/GET. But nothing happen, the two variables stay different and the status is still 0000 with no error. The screenshots and the project are attached. Thank you for your help ! David. AttachmentProject1.zip (61 Downloads) |
5/17/2016 5:35 PM | |
Posts: 33 Rating:
|
uncheck "optimized block access" in your receiving DB on PLC2. then recompile and download all. |