7/28/2018 5:29 PM | |
Joined: 10/9/2015 Last visit: 7/31/2024 Posts: 9 Rating:
|
Hello to everyone. I am using s71200 plc. There are 3 remote input and output modules connected to PLC. I want to make a CPU stop when any of the modules fail. please help me ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 7/30/2018 12:06:59 PMNew subject after splitting |
|
8/2/2018 8:47 PM | |
Joined: 3/16/2015 Last visit: 10/10/2021 Posts: 1250 Rating:
|
What are the remote I/Os? One way to run and stop the CPU is via HMI event so you can connect a PLC tag ( I mean any tag on PLC side) to a tag on HMI and set an event "Value Change" to "SetPLCMode>Stop". I tested it and it works but the HMI tag has to be connected to something otherwise it doesn't work. Not sure why so I connected it to animate a button. How the PLC tag is triggered is up to you and can range from diagnostic events to communication ones. |
8/2/2018 9:13 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating:
|
Hello, but why you want that the PLC goes into STOP mode? normally is the opposite, we do not know your process but putting a machine in a stop mode is dangerous, perhaps it is better to monitor the cards and go out with an alarm. |
This contribution was helpful to
1 thankful Users |
Follow us on