10/23/2005 5:55 PM | |
Posts: 5 Rating: (1) |
The 224 XP comes with 2 analog inputs and 1 analog output built into the CPU. What are the addresses for these I/O points? Appreciate any and all help. Thanks. |
10/24/2005 9:56 PM | |
Posts: 264 Rating: (59) |
Hello Paul, AI: AIW0 and AIW2 AO: AOW0 (AOW0 is reserved) Attention: If you don´t use a CPU224XP with integratet Analog Inputs but e.g. the 'normal' CPU224 and a SM231 extension module, the Adresses for this module starts at AIW0 !! You can find this information in the system manual of the S7-200 Chapter 4 http://support.automation.siemens.com/WW/view/en/1109582 best regards |
Last edited by: O_Moderator at: 12/14/2010 2:40 PMlink edited Last edited by: neo at: 10/27/2005 5:13 PMLast edited by: neo at: 10/25/2005 12:54 AM |
|
11/30/2005 10:45 PM | |
Posts: 5 Rating: (1) |
Thank you for your response and enlightenment. For the 224XP, is the analog output AOW0 or AQW0? |
12/15/2017 8:11 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by Kiiza is split to a separate thread with the subject After connection of signals to addresses aren't able to read any values. Best regards |