11/10/2011 6:27 AM | |
Joined: 3/24/2010 Last visit: 7/29/2024 Posts: 118 Rating: (1) |
Good day, I just want to seek an expert advise on this. I got an error which says "DP slave not accessible by means of the bus." I want to link my S5 ET200U (6es5-318-8mb12) to my S7 network but i keep on getting this error. I am using 313-2C DP as CPU and S5 ET200U with 2 slots rack and 1 DO module connected on the 2nd slot, slot1 is vacant. My profibus connectors at both ends are "ON". I dont know what to do to fix this problem. Please help me, i know someone knows how to do this. Thank you in advance. Daniel Attachmentpics.zip (149 Downloads) |
11/10/2011 7:48 AM | |
Joined: 10/7/2005 Last visit: 10/14/2024 Posts: 3024 Rating: (1054)
|
Hello try the following please and let us know if it helped: 1.) Movethe DQ module into the first Slotand only configure Slot "1" in your S7 HWconfig. 2.) Check and follow the advise in the FAQ below: Coupling ET200U DP (6ES5 318 8MB12) to an S7 master |
Cheers |
|
11/12/2011 8:15 AM | |
Joined: 3/24/2010 Last visit: 7/29/2024 Posts: 118 Rating: (1) |
both of them are in "IN" slot. I tried to switch the switch no. 8 but still did not work.. |
11/15/2011 4:07 AM | |
Joined: 3/24/2010 Last visit: 7/29/2024 Posts: 118 Rating: (1) |
Good day sir.. Ive done it already.. Thanks for the help. |
11/15/2011 4:45 AM | |
Joined: 10/7/2005 Last visit: 10/14/2024 Posts: 3024 Rating: (1054)
|
Hello Daniel Cyborg would you mind telling uswhat the problem was as this may help others in the future with a similar issue. |
Cheers |
|